Setting the SOC below 100% when operating the solar generator.

 

(@elteh)
Active Member
Joined: 2 years ago
Posts: 4
Topic starter  

Hello.

I set the soc to 90%. The house is connected to net metering and we installed an ATS switch. The storage will only be used for Peak shaving and island operation in case of a distribution failure. The problem is that when the solar power plant is operating, the batteries are charged to 100%. Is it possible to fix this?



   
Quote
(@elteh)
Active Member
Joined: 2 years ago
Posts: 4
Topic starter  

I resolved problem with "mode scheduler". When PV generator is working I set manual scheduler "Feed-in priority, Min SoC 90%"



   
ReplyQuote
Samantha Buckner
(@samb)
New Member
Joined: 2 years ago
Posts: 1
 

Hello please message into the service.uk@fox-ess.com and we can take a look into this if you haven't managed to solve this.



   
ReplyQuote
(@elteh)
Active Member
Joined: 2 years ago
Posts: 4
Topic starter  

@samb Thank you. It works fine now.

 

Best regards.

 



   
ReplyQuote
(@elteh)
Active Member
Joined: 2 years ago
Posts: 4
Topic starter  

The graph above shows that in "feed in priority" mode, the storage tank is charged to the desired 90%SOC with a power of 0.4 kW. Where can I set this charging power?

 

Thank you.



   
ReplyQuote
Craig Woollaston
(@admin)
Member Admin
Joined: 2 years ago
Posts: 34
 

The only setting that can dictate this is the battery charge current setting - but rate of charge can also be adjusted at high Soc levels or by temperature.  I might need the inverter serial number to take a look at the settings.



   
ReplyQuote